Engineer's Allure
This Forum is the only Pakistan's platform dedicated to engineering & science disciplines. So join us & open up channels for technical discussions. If you are a Professional Engineer or a Teacher Contact Us ...& you may be accepted as Forum Moderator Smile
Get the most out of our technical forum using these tutorials:

General Forum Usage
Insert real-time Math Equations
Insert Streaming Documents
Unblocking Youtube in Pakistan

Join the forum, it's quick and easy

Engineer's Allure
This Forum is the only Pakistan's platform dedicated to engineering & science disciplines. So join us & open up channels for technical discussions. If you are a Professional Engineer or a Teacher Contact Us ...& you may be accepted as Forum Moderator Smile
Get the most out of our technical forum using these tutorials:

General Forum Usage
Insert real-time Math Equations
Insert Streaming Documents
Unblocking Youtube in Pakistan
Engineer's Allure
Would you like to react to this message? Create an account in a few clicks or log in to continue.
Latest topics
» Tough Life of a Resin Bead
by ioncube Fri Jul 19, 2013 8:16 pm

» Final Year Projects Suggestions
by ioncube Fri Jul 19, 2013 2:48 pm

» Tracking Natural Gas Via Flowmeters
by ioncube Sat Sep 08, 2012 11:04 pm

» Maximising Heat-Transfer Fluid Life
by ioncube Thu Aug 23, 2012 6:16 pm

» Exercise your Brain
by ioncube Thu Jul 19, 2012 12:49 pm


Tracking Natural Gas Via Flowmeters

Go down

Tracking Natural Gas Via Flowmeters Empty Tracking Natural Gas Via Flowmeters

Post by ioncube Sat Sep 08, 2012 11:04 pm

With today’s increased emphasis on strategic energy management, many throughout the chemical process industries (CPI) and elsewhere are attempting to obtain better information on the natural gas consumption in their facilities. While custody-transfer flowmeters are typically in place at the property line (to track total gas consumption throughout the facility), the flow to individual combustion sources, such as heaters, furnaces, boilers and so on, generally remains unknown. When armed with better information on actual natural gas utilization, users can optimize the combustion performance by operating combustion processes at peak efficiency. Similarly, when users measure actual natural gas flow, they are able to determine which of their units is the most efficient. The operating efficiency of furnaces or dryers will vary. Knowing which process unit is the most efficient can result in significant cost savings. For instance, if more than one furnace, dryer or other type of gas-consuming unit is available, the user will be able to choose the combustion unit that provides the highest efficiency.

Tracking Natural Gas Via Flowmeters 2rrkscp
FIGURE 1. Insertion-style thermal mass flowmeters can easily be used in pipe with diameters from 1.5 in. and larger. The probe is used with a compression fitting, which provides easy installation and ensures a tight seal in the pipe

The first step to energy management and reducing the energy usage is to obtain good measurements of the flowrates of each individual combustion source. In addition to providing tools for improving energy management, the measurement of the natural gas utilized by individual combustion sources may also permit users to meet the regulatory requirements for determining emissions by reporting actual (rather than estimated) natural gas usage for each individual combustion source within the facility. In general, the pipe size for natural gas flow to individual combustion sources typically ranges from 1 to 6 in. The temperature of natural gas is typically at ambient conditions; rarely will you find natural gas at elevated temperatures. However, the pressure varies with the application. Because of this, flowmeters are generally located downstream of a pressure regulator. Line pressures typically range from 5 to 10 psig, and occasionally are as low as 1 to 2 psig. Even though the flowmeter is downstream of a pressure regulator, the actual pressure of the natural gas in the pipe may vary depending on the gas consumption. As the consumption increases, the line pressure may decrease.


Flowmeter options
There are many different ways to measure the flow of gases. A brief description of the leading options follows (see also Evaluating Industrial Flowmeters and Advances in Industrial Flowmetering, CE, April 2007, pp. 54–64). The difficulty in obtaining good, gas-flow measurements is the simple fact that gases are compressible, and thus the volume of the gas is dependent upon the pressure and temperature at the point of measurement. Chemical engineers will recall the basic concepts of the Ideal Gas Law, whereby gas volume is proportional to the temperature and inversely proportional to the pressure. This complicates gas flow measurement because, with the exception of thermal mass and Coriolis flowmeters, many gas-flow-measurement technologies measure the flow at the actual operating pressure and temperature. These units of measurement are typically expressed as either actual cubic feet per minute (acfm) or cubic meters per hour (m3/h). When comparing natural gas usage at various combustion sources for energy-management systems, on the other hand, the desired goal is to measure the flow relative to a defined pressure and temperature — at standard conditions (standard temperature and pressure; STP). While the definition of standard conditions will vary with different industries and in different geographic areas, when the flow is referenced to standard conditions, a mass flow measurement is obtained with units of measurement that are expressed as standard cubic feet per minute (scfm), standard cubic feet per hour (scfh), or normal cubic meters per hour (Nm3/h).
Flow measurement via orifice plate. This is the traditional method of flow measurement for both gas and liquids. In simplest terms, an orifice is a plate with a hole that is smaller in diameter than the pipe diameter. The orifice plate is positioned between two flanges. As the gas is accelerated through the smaller orifice, the pressure decreases, creating a lower pressure on the downstream side of the orifice plate. The flowrate is proportional to the square root of the pressure drop. Flow is therefore determined by measuring the pressure drop across the orifice plate. The important thing to consider is that the pressure drop is based on the flowrate at the gas density at the actual operating conditions. In order to get a mass flow measurement whereby the temperature and pressure are referenced to standard conditions, it is necessary to also have a temperature transmitter, a pressure transmitter, and a flow computer or multi-variable transmitter. As a result, while the cost of the orifice plate itself is relatively inexpensive, the installed price of the complete system becomes substantially more expensive when one considers the additional instrumentation that is required to obtain an accurate mass flow measurement. Another factor with orifice plates is their range and turndown. With the orifice plate or any flow measurement based on differential pressure, the signal (pressure drop) is at zero at no flow and then increases with the square of the flow as shown in Figure 3. Thus, if the user has an application requiring a 5-to-1 turndown in flow, a differential pressure transmitter with a turndown of 25-to-1 is required. This issue of turndown can create limitations with the application of orifice flowmeters. Similarly, when sizing an orifice to handle the maximum flowrate, it may not be possible to also measure the flow at the lower end of the range, due to loss of signal. The pressure drop across a flow element may be a consideration when looking at competing flow-measurement devices for natural gas. Generally, the flowmeter is installed downstream of the pressure regulator with line pressures potentially as low as 1 psig. Under these situations there may not be adequate pressure in the pipe to provide sufficient pressure drop to ensure accurate flow measurement.

Tracking Natural Gas Via Flowmeters 2h666ua

Vortex flowmeters. In a vortex flowmeter, a bluff object or shedder bar is placed in the flow path. As gas flows around this shedder bar, vortices are cyclically generated from opposite sides of the bar. This principle is seen every day when looking at a flag fluttering in a breeze. The flag pole is the bluff object and the fluttering of the flag is a visual indication of the vortices as they move across the surface of the flag. The frequency of vortex generation is a function of the gas velocity. Various methods, frequently relying on piezoelectric crystals, are used to detect and count the number of vortices. The relationship between the number of vortices shed from the bluff object with the flow is considered to be linear after some minimum flowrate has been reached, as determined by the Reynolds number. It is also important to realize that the measured flow is based on the actual gas density at the operating pressure and temperature. Thus, to convert the flowrate measured by a vortex meter to mass flow, the pressure and temperature must be measured (to adjust for changing gas density). When applying vortex flowmeters to applications involving natural gas flow, it is important to get complete process information including the minimum and maximum flowrate, the gas pressure and gas temperature. Because of the Reynolds number influence, when sizing a vortex meter to measure the minimum flowrate, it is often necessary to reduce the pipe size in order to increase the velocity to a range that ensures that vortices will be generated. This may complicate the installation of a vortex flowmeter in existing installations and may also increase the pressure drop.
Turbine flowmeters. Turbine flowmeters have wide application for natural gas flow measurement. The operation of a turbine is based on a freespinning rotor. As the fluid flows past the rotor, the rotor is turned with each revolution that corresponds to a given quantity of gas. There is a magnet in the rotor. The number of rotations are counted using an external pickup that provides a series of electronic pulses with each pulse equivalent to one rotation. The pulses are then sent to the transmitter. The manufacturer provides a K factor to relate each rotation to a given gas volume. The number of pulses that are counted over a given time period provide both the flowrate and the totalized flow. Turbine meters have relatively high turndown capabilities with corresponding high measurement accuracy. Like the previously mentioned flowmeter types, the turbine flowmeter is a volumetric device that measures the actual flow at the operating conditions and thus requires pressure and temperature correction to obtain accurate mass flow. Considerations when applying turbine meters include the cleanliness of the gas and the fact that there are moving parts in the gas stream.
Ultrasonic flowmeters. This technology measures the difference in transit time of pulses that travel from a downstream transducer to the upstream transducer, compared to the time from the upstream transducer back to the downstream transducer. While this technology is accurate and accepted by AGA (American Gas Assn.) for the custody transfer of natural gas, the suitability of this technology for measuring the flow of natural gas to individual combustion sources within a facility becomes questionable, considering the relatively low velocities, and more importantly, the high cost of this device compared to other technology options. (Note that AGA also accepts orifice plate, turbine and Coriolis flowmeters.) Flowrate is measured at the actual operating conditions, requiring pressure and temperature to obtain mass flow. Some ultrasonic flowmeters will require a higher pressure (for instance, some units require a minimum of 150 psi operating pressure).
Coriolis mass flowmeters. Coriolis flowmeters provide a direct mass -flow measurement by measuring the deflection of a vibrating tube. This is a true mass flowmeter, as it is insensitive to changes in pressure, temperature, density or gas composition. The Coriolis flowmeter is very accurate, with high turndown capabilities. Coriolis flowmeters often require the pipe size to be reduced in order to obtain the desired range measurement. While suitable for measuring flow to individual combustion sources, this approach becomes rather expensive and is rarely used for the in-plant measurement of natural gas.

Tracking Natural Gas Via Flowmeters 1phy7q

Thermal mass flowmeters. Thermal mass flowmeters (Figures 1, 2 and 4) provide an inferred measurement of the mass flow of the gases passing through them. Specifically, thermal mass flowmeters measure heat transfer that is caused as the molecules (hence, the mass) of gas flow past a heated surface. The relationship between heat transfer and mass flow is obtained during the calibration of the instrument. In addition to providing a mass flow measurement without the need for additional devices to correct for pressure and temperature (as is required with the other flowmeters, with exception of Coriolis devices), thermal flowmeters also provide the following advantages:

  • Higher turndown capabilities. A range of 100-to-1 is easily obtained with a thermal mass flowmeter. Some combustion systems may have a high natural-gas firing rate during initial warm-up operation and then, once the desired temperature has been obtained, the flowrate of the gas is typically reduced to maintain the desired operating temperature. A thermal mass flowmeter can easily handle this range, which may be difficult to obtain with other technologies
  • Simplified installation. An insertion device permits simplicity of installing the flowmeter using NPT (national pipe thread) connection, flange, compression fitting or even a complete retractable probe assembly. Using a “hot tap” permits the user to install the flowmeter without having to shut down the operation. The insertion design also permits the use of the same instrument in different pipe sizes. Some use the insertion probe as a semiportable instrument and reconfigure the transmitter for the different pipe sizes
  • Lower pressure drop. There is virtually no pressure drop when using a thermal mass flowmeter. This is advantageous in low-pressure applications where other technologies would consume operating pressure.

Today, thermal mass flowmeters from different manufacturers rely on different methods of operation and sensor designs. All methods accomplish the same thing, which is to provide a mass flow measurement. A cutaway of a typical sensor is shown in Figure 5. The sensor consists of two elements, one providing a temperature measurement of the gas, with the other element heated to maintain a desired temperature difference between the two RTDs (resistance temperature detectors). Some manufacturers use self-heated RTDs, while others use a separate heater. Because there is a heated element in contact with the natural gas, the user should ensure that the temperature rise of the sensor is less than the autoignition temperature of natural gas, and that the instrument has all appropriate agency approvals for use in hazardous areas. With this design, the electronics maintain a desired temperature difference between the two pins. At no flow, there is little heat loss and it takes little energy to maintain the desired temperature difference. As flow increases, heat is transferred from the heated sensor into the gas stream, the electronics detect the reduction in the temperature difference and apply more power to the heater to maintain the desired temperature difference.

Tracking Natural Gas Via Flowmeters 10oedtl

The typical relationship between mass flow and power is shown in Figure 6. The shape of this curve is very different from the comparable curve that was previously discussed for an orifice plate flowmeter (Figure 3). For instance, with a thermal mass flowmeter, there is a signal at low flow, and that signal increases rapidly, providing a great deal of sensitivity at low flowrates. This is why the thermal mass flowmeter is able to reliably measure much lower flowrates compared to competing flow-measurement technologies. Meanwhile, as the flowrate continues to increase, the amount of power required to maintain the desired temperature difference continues to increase — but not as rapidly — thus providing the higher turndown capabilities mentioned earlier. However, as the flowrate continues to increase, the sensor will eventually reach a state where it becomes saturated and unable to transfer any more heat into the gas. Calibration of the thermal mass flowmeter is required to establish this relationship between mass flow and heat transfer.
Calibration involves placing the flowmeter in a test bench, flowing a known amount of gas past the sensor, measuring the signal, and repeating the process at different flowrates. At least ten calibration points should be obtained over the calibration range of the instrument for best results. These data are analyzed and the calibration data are then loaded into the instrument. After calibration, the flowmeter will provide a linear output signal over the calibration range. Because of the heat-transfer characteristics of the sensors, each individual sensor must be calibrated. Once calibrated, the user can reconfigure the instrument for a lower flow range to accommodate those situations where the initial flow may be low, and then increase over time as production in the facility increases.
We have previously shown that thermal mass flowmeters provide a mass flow measurement based on the thermal properties of the gas, and thus, temperature correction for density adjustments are not required when going from actual operating conditions to standard conditions. However, it is recognized that the thermal properties of the gas will change with gas temperature. Thus it is important that the thermal flowmeter have realtime temperature compensation, to continually adjust the flow measurement for variations in the process gas temperature. Various manufacturers deal with the issue of temperature compensation differently, with some manufacturers providing temperature compensation as a standard offering; with these designs, the instrument also measures the gas temperature and adjusts the flow measurement for variations in the thermal properties of the gas with temperature. Thermal flowmeters will provide a 4–20-mA output signal that is linear with the flowrate. A built-in software totalizer is also available, with the totalized flow shown on the display for those users who want to obtain the total consumption of the natural gas over a given time period. Those designs that also measure the gas temperature as part of the realtime temperature compensation also have the ability show the temperature on display of the flowmeter. Units with HART communication have the ability to transmit the mass flow, temperature and totalized flow as part of the HART data stream. Other units may also provide a pulse output and a milliamp signal of the temperature. Changing gas composition will affect the heat transfer characteristics of the gas and potentially create an error in flow measurement. This is most prevalent when a significant change is made in the type of gas that is flowing through the unit — for instance, using a thermal mass flowmeter that was originally calibrated for air in natural gas service.
Fortunately, minor changes in the composition of natural gas, such as a reduction of methane content with a corresponding increase in the ethane content, will have very minor changes on the overall flow measurement that is produced by a thermal mass flowmeter. Using this example, the density of methane and ethane are considerably different, which will have a significant effect on other flowmeter technologies (such as those based on the measurement of differential pressure) where the gas density is directly used in the flow measurement. With thermal mass flowmeters, the gas density is only one of the factors that affect convective heat transfer. Variations in methane and ethane content of the natural gas can create a change in the heat transfer characteristics of the natural gas (and slightly affect the flow measurement). However, the relative change in heat transfer is comparatively less than the change in gas density, which is directly used by other flowmeters.

Tracking Natural Gas Via Flowmeters 11100m1



Installation considerations
Nearly all flowmeters require some straight run of pipe ahead of the flow sensor. Thermal mass flowmeters follow the same basic guidelines. The flow calculations used with an insertion-type flowmeter assume the presence of this fully developed flow profile and the placement of the sensor on the centerline of the pipe as shown in Figure 7. Theoretically the velocity at the wall is zero and the velocity on the centerline of the pipe is 20% higher than the average velocity. This illustration also shows the use of a compression fitting that is commonly used for inserting the probe into the pipe. Because the flow profile at the centerline is relatively flat, minor variations in the insertion depth of the sensor will not have any impact on the flow measurement. Theoretically, this desired flow profile occurs with a straight run of pipe whose length is the equivalent of approximately 20 pipe diameters. This is the general guideline for the amount of straight run following a single elbow, while longer lengths are required following a double elbow. In many cases, this amount of straight run may not be available. When this is the case, options that are available include the use of a flow body with a flow conditioner as shown in Figure 8. This design ensures that the desired flow profile at the sensor is obtained. The use of a flow conditioner reduces the straight-run requirements. Or, the user may accept a reduction in the absolute accuracy due to the presence of the non-uniform flow profile, realizing that the flow measurement will continue to be repeatable. If using an insertion probe, another installation effect that is not frequently realized is the correctness in pipe size. The inner diameter (ID) of the pipe or the pipe area is entered into the transmitter.
Users will frequently specify pipe size such as 4-in. Schedule 40 in which case the manufacturer utilizes the pipe dimensions from the standard pipe tables. What many users may not realize is that the dimensions in the pipe tables are nominal dimensions, and in reality, the wall thickness of the pipes may vary, resulting in corresponding variations in the pipe ID. Since the pipe area is a critical factor in calculating the mass flow, any deviation between actual pipe size and the nominal dimensions will cause errors in the flow measurement. It is generally possible to enter correction factors in the transmitter to adjust for non-uniformity of the flow profile, pipe size or other installation effects. However, this requires that the user have a valid basis for comparing the measured mass flow with the expected flow.
Biogas measurement
Considerations related to the measurement of biogas using thermal mass flowmeters are very similar to those for natural-gas flow measurement. The primary difference is that biogas composition is typically a mixture of methane and carbon dioxide, with the potential trace concentration of other gases depending upon the application. Typically, this ratio is 65% methane and 35% carbon dioxide. Biogas can come from a number of sources including anaerobic digesters, landfill operations, and organic-industrialwaste processing. Other distinguishing issues with biogas is that the gas is often wet and may also be dirty. Biogas measurement systems frequently operate at relatively low pressures and low flowrates. The combination of low flow, low pressure, and a wet and dirty gas rules out most other technologies, due to lack of sensitivity at low flowrates and difficulties with the potential buildup of particulate matter on the flow element. By comparison, thermal mass flowmeters (Figure 9) are particularly well-suited for biogas/digester gas-flow measurement, due to the low flow sensitivity and low pressure drops. The use of an insertion probe with a retractable probe assembly eases the periodic removal of the probe for cleaning. There are many flow-measurement technologies that can be used for the measurement of natural gas and biogas. However, thermal mass flowmeters provide certain advantages in terms of mass flow measurement, turndown, flow sensitivity, low pressure drop and ease in installation. In fact, thermal mass flowmeters tend to allow for very economical installations, thereby providing the lowest installed cost compared to other technologies that require pressure and temperature compensation.


Author
Wayne Shannon is the thermal dispersion product manager at Magnetrol International Inc.
ioncube
ioncube


Teacher & or Working Engineer
Country : Pakistan
Male Posts : 45
Likes Total : 7
Join date : 2012-02-02
Location : Lahore/Faisalabad

Back to top Go down

Back to top

- Similar topics

 
Permissions in this forum:
You cannot reply to topics in this forum